Inventor error codes

Display codes

Inventor F5

Outdoor fan speed out of range

Inventor – Aria AR5 (AR5VI / AR5VO)

Ranges
  • Aria AR5
  • Outdoor unit
  • Also shown as EC07
  • Lamps: run lamp blinks 6×, timer lamp lit

Likely causes

Fan motor, its wiring, outdoor PCB.

First checks

Turn the fan by hand (blocked?) → check the voltages at the motor connector → replace the motor or the PCB.

Note

Only on some models.

Source: Inventor Wall Mounted Unit Service Manual V:1.0.062022, ManualsLib page 102

Inventor U6RSL multi split (Midea-built)

Ranges
  • U6RSL multi
  • U5MRSL multi
  • Lamps: run lamp blinks 6×, timer lamp lit

Likely causes

Fan blocked, wiring, fan motor, outdoor PCB.

First checks

Turn the fan by hand → check the wiring → check the PCB's output to the motor: the phases should be equal.

Source: Inventor Multi Split Unit Service Manual V:1.0.062022, p. 31, 48

Inventor U6RSL multi split (Midea-built)

Ranges
  • U6RSL multi
  • U5MRSL multi

T2B sensor of room E missing or faulty

Likely causes

Sensor, its connector.

First checks

Check the connector → measure the sensor's resistance against its R-T table.

Source: Inventor Multi Split Unit Service Manual V:1.0.062022, p. 32–33

In the app you also find codes by the model number on the nameplate, and Diagnose judges your readings.

Open in the appAll Inventor error codes