Midea error codes

Indoor unit codes

Midea F0

Over-current protection

Inventor U6RSL multi split (Midea-built)

Ranges
  • M2OH / M3OE multi
  • Lamps: run lamp blinks 1×, timer lamp lit

Likely causes

Refrigerant system, outdoor ambient above 50 °C, poor ventilation, dirty outdoor coil, blocked pipe, main board.

First checks

Measure the input current → check the airflow and the outdoor coil → look for a blocked pipe → replace the main board.

Note

Only on some units.

Source: Inventor Multi Split Unit Service Manual V:1.0.062022, p. 31, 50

Midea – old 2-character codes (about 2017–2019)

Ranges
  • Oasis Plus 2018

Overload current protection

  • Outdoor unit
  • Lamps: run lamp blinks 1×, timer lamp lit

Likely causes

Supply, blockage in the system, compressor, reactor.

First checks

Check the supply → look for a blockage → measure the compressor windings (KTN110D42UFZ: 1.82 Ω) → wiring → reactor → outdoor PCB.

Source: Oasis Plus 3D Inverter Series 2018 Service Manual, R32, p. 69

In the app you also find codes by the model number on the nameplate, and Diagnose judges your readings.